Venice warns homeowners to beware of air duct cleaning scams, especially the sort where unscrupulous cleaners offer a $49 special deal but start piling on extra fees. “It’s a bait and switch scam where they say they’ll offer unlimited cleaning, but then they throw around terms you might not understand, such as extra fees for a ‘main duct line,’” he says. “And many times, these cleaners end up walking out the door with twice the amount of money a reputable duct cleaner would charge. They’ve gotten very sophisticated at upselling.”
On the other hand, if a service provider fails to follow proper duct cleaning procedures, duct cleaning can cause indoor air problems. For example, an inadequate vacuum collection system can release more dust, dirt and other contaminants than if you had left the ducts alone. A careless or inadequately trained service provider can damage your ducts or heating and cooling system, possibly increasing your heating and air conditioning costs or forcing you to undertake difficult and costly repairs or replacements.
What if you move into a 20 year old house and find that the people who owned it previously NEVER replaced the filter? It was so dirty that the HVAC system did not work at all. For most people - duct cleaning is NOT a waste of time or money. You must not have allergies. I have very bad ones plus asthma. It makes it very hard for me if I don't get it done every few years. By the way - the ducts get dusty just sitting there - especially without air going through them. Dust settles on them just like it does the furniture.
I’m a heating and air conditioning contractor. I’ve been in the trade for over 15 years. I’ve witnessed numerous duct cleaning projects and talked with many duct cleaners. Duct cleaning as it’s usually promoted is a fraud. Most duct cleaners claim to deliver cleaner air. They deliver exactly the opposite. The studies on duct cleaning prove it, including a May 1998 study sponsored by NADCA and the EPA! The stories are compelling, but they can come up with stories that “prove” anything they want. Internet searches are dominated by results from those who are paid to tell you that duct cleaning is worthwhile. Search a little more and you’ll find the truth.
A house breathes just like you an I.For example every time your clothes dryer comes on it automatically creates a negative pressure inside the home.So if air goes out of the living area it has to be replaced.....now look above the ceiling fan ....you see the cover...underneath that is a hole straight to your attic....Now the stuff on your ceiling fan you call dust...call it insulation,rat fecies or anything else that is in your attic that could be pulled in your due to a negative pressure.

The Environmental Protection Agency says that “duct cleaning services typically – but not always – range in cost from $450 to $1000 per heating and cooling system, depending on the services offered, the size of the system to be cleaned, system accessibility, climactic region, and level of contamination” and type of duct material. Consumers should beware of air duct cleaning companies that making sweeping claims about the health benefits of duct cleaning – such claims are unsubstantiated. Consumers should also beware of “blow-and-go” air duct cleaning companies. These companies often charge a nominal fee and do a poor job of cleaning the heating and cooling system. These companies may also persuade the consumer into unneeded services with and/or without their permission. (If you have knowledge of a practicing “blow-and-go” air duct cleaner, contact your local Better Business Bureau to report the company, and your local, federal, and state elected officials to demand legislation.)
I purchased one of those Amazon air duct cleaning coupons for 49.99. When the company showed up, they removed the vent closest to the air intake and immediately told me I needed $1800.00 for all new duct work. They said they could not clean the system until new duct work was installed. I thanked them and said I would give them a call. The only call I made was to Amazon to get a refund. I know I didn’t need new duct work. Be careful to not fall for unscrupulous salesmen and their pitches and scare tactics.
Most organizations concerned with duct cleaning, including EPA, NADCA, NAIMA and the Sheet Metal and Air Conditioning Contractors' National Association (SMACNA) do not currently recommend the routine use of sealants to encapsulate contaminants in any type of duct. Instances when the use of sealants to encapsulate the duct surfaces may be appropriate include the repair of damaged fiber glass insulation or when combating fire damage within ducts. Sealants should never be used on wet duct liner, to cover actively growing mold, or to cover debris in the ducts, and should only be applied after cleaning according to NADCA or other appropriate guidelines or standards.
Once i received a call from a Person he Named Steve and He told me that he is from some like GTA Home services and providing Air duct Cleaning in around 105$ and i booked an appointment because he convince me in very will mannered so i agree the services i placed an order and i don't think that they guyz do a great job as he describe but they do same as he told me on phone i'm just surprised that they do a great job and they provide me free inspections of furnace and A/C as well and they really do a great job and they don't waist my money and time. thanks Adam Stevenson and GTA home service Team.
And if you have flex duct and/or fiberglass ductboard in your home- the last thing you want is a big brush or anything abrasive running through it. Even high-pressure air can erode ductboard so I wouldn’t clean it with anything. If it becomes contaminated, get rid of it and install real ductwork. If your ductwork is accessible in the basement – the best thing to do is take it down and manually clean it if it’s full of junk. It’s not going to cost a nickel more to do that than to pay $500-1000 for a ‘duct cleaning machine” AKA big blower and vacuum – to do the job.

The next step was cleaning the cold air returns. He found a good spot to drill an 8” hole for his vacuum hose. The procedure matched the other air ducts except that when he finished at the two cold return registers he drilled several holes in the cold ducts in the basement and blasted air into them. Because of our houses age and the upgraded return system, I noticed that the main sheet metal return duct had no top but was just butted up against the ceiling in the basement. When he blasted air in, dust and crap shot out the edges along the ceiling. Once he finished that he removed the filter and “swept” out anything at the bottom of the return with his hand into the 8” hose.
It’s 11 years plus in the industry I have only had to sanitize two systems both were slab systems that were in concrete and could be cleaned with a different method than normal duct cleaning. We were able to use water to rinse out the disinfectant. Would you use a chemical on anything else you use to eat or drink with and not rinse it off? The ducts in your home should be thought of as your homes heart and lungs and breathe the same air that you do. And just like us we wouldn’t use bad chemicals in our lungs and heart.
As I type this, I am having my ducts cleaned. About 30 including returns and the furnace. $543.00. I am watching the team do it and can see the clear vacuuming tubing and how dirty it has become. I like the gentleman’s comment on “stick your head in your vacuum and breath”….I get it. The team showed me the machine and it’s filtration system…and they will show me it again after the cleaning. However, like I said before, I am actively seeing the tubing that is clear before they start and how dirty it is once they begin and continue cleaning. Reputable company and not a “fly by night” coupon service. People don’t be so cheap, that is your problem.
I turned on the AC when he was finished and immediately saw black fuzz balls the size of marbles come out of several of the registers. He said that was expected since everything was shaken up. So much for describing the service as cleaning. I paid him and sent him on his way. I cannot imagine that this type of service is worthwhile in anything but a new house. Apparently in old houses such as mine I can expect that using a whole house humidifier in the winter followed by a great AC can loosen the soot. Maybe this is to be expected for the first few weeks of summer each year. I now have lined the inside of the registers with cheesecloth to catch the fuzz. I’ll see if it stops after a couple of weeks.

My vent covers have lots of mildew. They look bad! I live in a very humid climate in a condo. The handyman here has offered to take those down, wash them, sand, & then spray paint them with a mildew resistant paint. He said that he will leave them off overnight to dry. I am wondering if this is safe to breath the AC blowing out into the open all night??. ! Guess it is better than the mildew!?
#3 The ONLY time Duct cleaning is needed is when the home had a fire, Bad roof leak on to FIBERGLASS ductwork or house sat vacant for many years with out the air running. And its better to replace than to do “abrasive” duct cleaning. If the duct cleaning has a rotating brush it will remove part of the glue that is holding the Fiberglass in the ducts together, PERIOD no matter how much the say it don’t because the brush is soft.
I know it has to have a new concentric venting system installed, I believe it needs new plenums ( mine are rusty but both of these require extra work , so someHVAC persons are saying I do not need either!! RED FLAG THERE. Also, it will need a new drain using PVCP ?? Piping run maybe two, depending on where my evep coil drain is conected (here in TN they use to run them in with the septic lines, now they cannot be run through that way), Lastly I am not where or what these things do beides hold water but I was told It needs a filter rack and new filter base safety pan. THATSSS it that is all I know about this stuff aside from the fact that nothing up there is to code thus far LOL. !!
The short answer is yes, duct cleaning, done right by a reputable company will help with the smell. It is likely though the smell is coming from another source, ie the crawl space. It could also be that another rodent is dead in the duct work. A visual inspection would be in order to check for any breach in the duct system. A duct pressure test would be able to tell you how much air is leaking from the system over all. A hole large enough for an animal to enter would loses a great deal of air, over 300 CFM. It would be worth looking into having this test done and it should cost around $200. Cleaning the air handler and evaporator coil will greatly improve the performance of the air conditioner. Dirt and dust on the evaporator acts as insulation and reduces the amount of cooling done be the coil. Any quality duct cleaning should include cleaning the air handler and coil, and the tech should allow you to watch him perform the work as it is done.

Maybe I took him to literally but I am pretty sure cops wont show up to ensure that my duct gets replaced. He said it would be over 1000 dollars to replace the ductwork if that is the case. Now, I spoke to a friend who did 2 ductwork lines on his own in his attic and he said it was like 15 dollars for the plastic wirewound tubing to create new ducts. Should I cancel that appointment and just do the work on my own? I feel like I’m a chump or lazy for considering paying someone to do this work.
The bottom line is: no one knows. There are examples of ducts that have become badly contaminated with a variety of materials that may pose risks to your health. The duct system can serve as a means to distribute these contaminants throughout a home. In these cases, duct cleaning may make sense. However, a light amount of household dust in your air ducts is normal. Duct cleaning is not considered to be a necessary part of yearly maintenance of your heating and cooling system, which consists of regular cleaning of drain pans and heating and cooling coils, regular filter changes and yearly inspections of heating equipment. Research continues in an effort to evaluate the potential benefits of air duct cleaning.
As a homeowner and an owner of rental property I can tell you that the air ducts sometimes need to be cleaned. If you have had pets or anyone smoking in your home (even a visitor) for any length of time, having the ducts cleaned is really good idea. I had a tenant who did not smoke, but got married to a smoker more than year after moving in. When I realized someone was smoking I had them move out, but the smell was awful. I had the ducts cleaned and sanitized (it was a bit extra). The ducts were shiny like new afterwards. I left the windows open for a few days and we cleaned the place super clean and then replaced the carpets. The duct cleaning was worth every penny because the house looked, smelled, and felt new afterward. I plan to have my own house ducts cleaned again this year as we have two cats. We had them cleaned about 12 years ago and they found building materials in the ducts! If you move into a house that has never had them cleaned, it is good to do it. If you have allergies, clean the ducts to see if it helps. You never know what is in your ducts if you have never had them cleaned.
Here in Frisco, TX…just had a tech come out to clean vents. I used a 30 bucks groupon for “complete vent cleaning”. He told me I have 3 AC units and groupon covers only 1. I told him to do the unit upstairs where the kids sleep. He decided on his own to do the downstairs unit. I yelled at him why he is not doing the unit I told him to do! He said they are all connected. I will clean two for you for the price of one… Oh really?
I can’t believe I got ripped off by this Air Duct Cleaners. I called them for this $63 coupon per furnace unlimited vents then when they came after he checked it all I hear is I have molds and leak all is worth $499, $799, $899 per furnace but I told him to just clean the duct and patch the single leak per furnace worth $38 each. Still eanding $899 total. All the work he done is in less than an hour he didnt even go to each vent to clean it. All he did is to path the air leak on that entry pipe to the furnace and open the main venting system, vacuum it, and wash the floor of the vent with a solution. Overall time is about 20 mins talking with me discussing all the option which thinking they made me think I don’t really have an option and 40 mins wash and vacuum he took pictures of before and after of only one furnace. He gave me a receipt without the details on what he has done in the house just the name and price. I think we may need a strict law to punish and control all this companies who do this so other company who do good will despise them.
Hello, I read your comment and I know it was two years ago but I hope you see my message. I am trying to figure out what to do as I was told that there is some cat odor in the finished basement. I think with the air conditioning running that it may carry odor. The litter boxes are always kept clean. I wonder if odor can be trapped in the ducts, if Air Duct Cleaning could help, but it is quite expensive plus I'm concerned that it may not help. Please elaborate as to why you think it doesn't work that well. Do you have any other advise? Did you work in the field of Air Duct Cleaning? Thanks so much!
Just had my air ducts cleaned. They used a high pressure air hose in all the heat ducts and cold air returns. He showed me the stuff that came out, the reason for the duct cleaning was the fact that I had a problem. With rodents. There was quite a few mummified rats and mice, and he said I wouldn’t have to have them done again unless I incur another problem or have renovations done. Cost me 345.00 for a 2 storey large old home. Not a bad price as I had them done when I moved in 28 years ago and it cost me 500.00. Lots of dog hair, toys, balls and assorted goodies came out as well. Took them 2 hours. I did have sanitizer put in the ducts because of the dead rodents.
fact is most homes have bad filter racks. when you insert the filter it doesn’t seal well to the sides so some of the air and dust bypass it and end up in the supply ductwork and into the house. Most of the dust in the supply ductwork settles down and doesn’t get blown in the house but some of it does when the blower starts up or when you put a new filter. If you have allergies or other health problems put in an electronic air cleaner, get your ducts cleaned and run the fan as much as you can afford. you can also get an ECM motor installed which is going to be worth it if you want to run the fan 24/7. If you have uninsulated metal ducts take down the ones you can and wash them. Then put them back and seal the joints. Cleaning the ductwork also improves airflow which is important to AC and Heat pump systems for efficiency. An electronic air cleaner will also improve airflow and static pressure because they usually have a much larger filter surface area. An electronic air cleaner also keeps the ac coil clean like new which means better efficiency and no cleaning needed. AC furnaces sometimes grow mold around the coil because of the condensation. Electronic air cleaners should be able to filter mold spores but the best remedy is installing a UV light next to the coil which will kill the mold.
Just had my air ducts cleaned. They used a high pressure air hose in all the heat ducts and cold air returns. He showed me the stuff that came out, the reason for the duct cleaning was the fact that I had a problem. With rodents. There was quite a few mummified rats and mice, and he said I wouldn’t have to have them done again unless I incur another problem or have renovations done. Cost me 345.00 for a 2 storey large old home. Not a bad price as I had them done when I moved in 28 years ago and it cost me 500.00. Lots of dog hair, toys, balls and assorted goodies came out as well. Took them 2 hours. I did have sanitizer put in the ducts because of the dead rodents.
I was told that 15 out vents would be cleaned and one main vent. the guy came over and gave me an estimate of $500. I had acquired a groupon for $49. the guy said just doing the out vents and one main vent would accomplish nothing. Now I am in dispute with the groupon people for a refund which they won’t give and have to go ahead and waste the money and let them do it. Is their doing the 15 outvents and one main one going to accomplish anything?
You should be aware that although a substance may look like mold, a positive determination of whether it is mold or not can be made only by an expert and may require laboratory analysis for final confirmation. For about $50, some microbiology laboratories can tell you whether a sample sent to them on a clear strip of sticky household tape is mold or simply a substance that resembles it.
×