Despite Bergendahl's experience, Vinick says NADCA's certification standards have improved the situation. "A lot of [service companies] weren't going about it the correct way," he says. “We have an anti-fraud task force, and we’ve gone after some fraudulent duct cleaners with the help of state attorneys general.” He suggests that in addition to NADCA membership, homeowners make sure their cleaners are an established business, have appropriate insurance and are registered to do business in their state and locality.
If the system is sealed air-tight and a really good filtering system is in place then you should NEVER have to clean your ductwork. Most dust people see in their homes (on beds furniture etc....) is broken down insulation that is being blown into the home from the attic (venturi effect) where the duct bucket (box etc...) is not sealed at the sheetrock ceiling. On the return side, ANY leaks in the ductwork will pull hot attic air and dust into the system, clogging up everything.
I read your article with interest and think it is a good start. One service that is always talked about is fogging ductwork for sanitizing. Many companies offer this service for disinfecting or adding a clean smell to the ductwork. Before any chemical or disinfectant is used, please read the MSDS (Material Safety Data Sheet). You might be surprise on what you are putting into the air stream. This is a high profit service and should be explored thoroughly before purchasing,
On average, we (Indians in Ontario) receive 3-5 calls per day for duct cleaning services from India. I did get ducts cleaned twice in 25 years. For a newly built house, it should be done as material goes into the ducts. Every year, before turning the heat on, I clean the ducts, using the vacuum pipe or with wet towel. Most of the dust, pet hair, small items get to the ducts from the top floors, not where system is installed. Even in winter months, I open 2-3 windows for air circulation for 15 minutes, specially right after cooking, almost daily. We breath in the same stale air, develop health issues. Also, I have an added air cleaning and fileration system installed. At a low rate, this system constantly cleans the inside air and also that it pulls from the outside. Duct cleaning is a scam, there are other efficient and cost effective methods we can use to purify the inside air.
Moisture can enter the duct system through leaks or if the system has been improperly installed or serviced. Research suggests that condensation (which occurs when a surface temperature is lower than the dew point temperature of the surrounding air) on or near cooling coils of air conditioning units is a major factor in moisture contamination of the system. The presence of condensation or high relative humidity is an important indicator of the potential for mold growth on any type of duct. Controlling moisture can often be difficult, but here are some steps you can take:
I read your article with interest and think it is a good start. One service that is always talked about is fogging ductwork for sanitizing. Many companies offer this service for disinfecting or adding a clean smell to the ductwork. Before any chemical or disinfectant is used, please read the MSDS (Material Safety Data Sheet). You might be surprise on what you are putting into the air stream. This is a high profit service and should be explored thoroughly before purchasing,
The jury is out on whether or not cleaning your air ducts and vents has a significant enough impact to be necessary. A proven connection between immaculate duct systems and air quality in the home has not been made. However, if your vents display any of the signs listed above, cleaning would certainly be in your best interest. Allowing mold, debris and bacteria to fester could create bigger problems down the line. If having your system disinfected is within your budget, you may prefer to take care of these issues rather than ignore them.
My 48 yr old house (mine for the last 4 yrs) has considerable dust in the return plenum (fiber duct). I’m remodeling and recently re-sealed the return plenum AND the site-fabbed transition built when the new unit was installed, 2013. The return was leaky no doubt drawing musty, dusty air from the crawl space due to the Red-Neck fab & seal job! Pitiful craftsmanship! It took me 7 hours to fix the new transition piece. Anyway, the dust in the house is the same “color” as whats in the return duct and I’m getting way too much & too often in the house. I’ve also cleaned my coils, which were not that dirty.
In some older homes, there was a grey Mylar flexible duct. After years of use, it started to decompose. A duct cleaning company can come out and find why your air is so dirty and why your building doesn’t heat or cool like it used to. This is a savings on your part. You could also be sucking in Hot, dirty attic air. However, sometimes when a duct cleaning company comes out to clean it, the old duct can be destroyed and have to be replaced. Someone with little experience can replace this ductwork but if it isn’t done right it can ruin a lot of things and cost a lot in repairs.
I am NADCA Certified Air Systems Cleaning Specialist. Over the years I have learned on simple answer to this questions: there air duct cleaners and there are pretenders. There will be no benefit at all if you use on the very cheap pretender because they will not really clean anything. On the other hand if you call a qualified air duct cleaner with a NADCA Certification you will, like 99% of my customers, report improvement with your respiratory problems, you will see less dust and the job will pay for itself with energy savings and repair prevention.
in response to this reply " should your ducts be cleaned", i have to politely correct the person who answered this. you are not using common sense. first, most of the country uses metal duct work, so for you to say what you did, is wrong. second, the duct system in a house is a circulatory system. that means it draws air into the furnace, it gets filtered, and then it is blown out into the house to heat or cool. So, obviously that air is being brought into the house from somewhere right? Yes, its coming from the outside where there are many allergens and dust particles . For you to says that about whether a duct system is sealed or not, makes no difference. The air is coming from somewhere right? It has to originate from somewhere right? Just look on top of your cieling fan. If there is a bunch of dust up there, then there is obviously a bunch in your ducts. And the duct air is being circulated every day, and every hour through your house. Its simple, dust collects everywhere in your house. Imagine if you never dusted your shelves, or tv? There would be a ton of dust after a while. Well, now think about the air in the duct system. Of course theres gonna be a ton of dust in there. For you to say that it is not benififcial to clean the ducts, is plain ignorant. 90% of the air we breathe is in our household. Wouldnt you want that air to be as dust and allergen free? I could go on for hours about the benifits of duct cleaning, but i just wanted to make a quick point that the person whose says it is not benificial to clean them, is not using common sense. Not to mention, giving the people who clean ducts for a living, a bad name. Use your head .
Did you know that cleaning your ducts and vents can help airflow and increase energy efficiency? According to the Environmental Protection Agency (EPA), keeping your air ducts and vents clear can increase energy efficiency and indoor air quality. While the cost to clean ducts and vents might sound high, the benefits to homeowners–especially those sensitive to allergens–is worth considering.
I agree that good filtration and a sealed system will prevent the need for duct cleaning. However, when we do get called it is because the duct work has reached a noticeable state of restriction or dust or the homeowner is hyper-sensitive to these pollutants in their home. Most of the time we find that no filter or a cheap (99 cent) filter is being used or they have serious duct leaks in the system. If you are hiring a cleaner make sure they are using professional cleaning equipment which will consist of a rotating brush system and a vacuum source. Be highly skeptical of the contractor with no branded system or the guy who shows up with just chimney brushes and a shop vac. He will not be able to reach around all the corners or all the runs in your system and he will be taking your money for a superficial cleaning at best. Only trust a company that offers VIDEO inspection and more importantly.... a contractor who repairs, installs and seals ducts if a problem is discovered or heaven forbid, created. Good luck and get your ducts sealed if you do have a leak! It is one of the greatest energy losses to a home other than being poorly insulated.
I think that the coding and permit industry is a joke!! They will not allow the homeowner to apply for the permit it has to be the licenced contractor. It would make since to allow the homeowner to apply for this. But it is all about money!! They really don't care if its up to code because if they did then they wouldnt care who applied and payeed for it, but they want the contractor to do it so if they do something wrong they can fine them instead of just pointing it out and allowing them to do it right.
Air duct cleaning service providers may tell you that they need to apply a chemical biocide to the inside of your ducts to kill bacteria (germs) and fungi (mold), and prevent future biological growth. Some duct cleaning service providers may propose to introduce ozone to kill biological contaminants. Ozone is a highly reactive gas that is regulated in the outside air as a lung irritant. However, there remains considerable controversy over the necessity and wisdom of introducing chemical biocides or ozone into the duct work.
Furnace cleaners are mostly young men, I know this, I have been one for 15 years or so……so heres the truth, if there are any allergies, children, older people with health issues, we are GOING to make money. do not tell the company you have hired about any health complication. they are salesmen. and they don’t care about you. or your money. make sure they do a good job, then kick them out. you don’t need all the bells and whistles they wanna sell you. any idiot can clean duct work, like I said, I am one of them. I am very good at it, but I don’t have the back bone to sell a widowed old lady a humidifier that she doesn’t need for 500 bucks, overall, if you think you need this service done, which you probably don’t, get it done, do not spend anything over 300$ and do not do it again for at least ten years.
The most effective way to clean air ducts and ventilation systems is to employ Source Removal methods of cleaning. This requires a contractor to place the system under negative pressure, through the use of a specialized, powerful vacuum. While the vacuum draws air through the system, devices are inserted into the ducts to dislodge any debris that might be stuck to interior surfaces. The debris can then travel down the ducts to the vacuum, which removes it from the system and the home.
As a person with severe mold allergies, I live in a the South where the climate naturally breeds molds.We noticed a difference when we had our ducts cleaned.The company used a vacumn type system and covered all of our vents with plastic that was held up by the suction. We had no damage, no leaking dust/dirt back into the house and it took several hours. I think if you use a reputable company it makes the world of difference. Now we use better air filters and also have a UV light to prevent mold growth on ours system.We 'd do it again when the time comes. From your car's air filter to your dryer...anything works more efficiently when it is not filthy dirty.That's just common sense.
I am NADCA Certified Air Systems Cleaning Specialist. Over the years I have learned on simple answer to this questions: there air duct cleaners and there are pretenders. There will be no benefit at all if you use on the very cheap pretender because they will not really clean anything. On the other hand if you call a qualified air duct cleaner with a NADCA Certification you will, like 99% of my customers, report improvement with your respiratory problems, you will see less dust and the job will pay for itself with energy savings and repair prevention.
Duct cleaning is a complete scam, I was a “duct cleaning technician” for a whole week before I was fired for not upselling elderly widowed women $2000 extra for “toxic mold remediation” when their ducts were spotless to begin with. The last two days I was employed there I worked as a “helper” alongside a technician thats been with the company 7 years. He scammed every customer on mold and would at times get as much as $2500 extra for treating “toxic mold” in a typical 3 bedroom house in the suburbs. Wait…it gets even better, the “Biocide” the company used was simply a cheap $4.99 per gallon bought at Home Depot air freshener with no anti-microbial properties that was fogged into the HVAC system for 5 minutes, maybe using 1/2 cup of the stuff. In order to provide the customer with evidence of “mold infestation” the technician would be given bogus mold tests that always resulted in “toxic spores present” regardless if you swabbed the actual duct or nothing at all. Not to mention the actual duct cleaning job (typically $400) did basically nothing and the homeowner could’ve done a better job with a shopvac
I purchased one of those Amazon air duct cleaning coupons for 49.99. When the company showed up, they removed the vent closest to the air intake and immediately told me I needed $1800.00 for all new duct work. They said they could not clean the system until new duct work was installed. I thanked them and said I would give them a call. The only call I made was to Amazon to get a refund. I know I didn’t need new duct work. Be careful to not fall for unscrupulous salesmen and their pitches and scare tactics.

The amount of time it takes to clean a residential HVAC system depends on many variables such as the size of the home, the number of systems, the extent of the contamination and the number of HVAC cleaners performing the job. Ask at least two contractors to inspect your system and give you a time estimate for your particular system. This will give you a general idea of how long the job should take as well as an idea of how thoroughly the contractor plans to do the job.


When water damage strikes, you need to act quickly. Time is of the essence. We're available 24/7 to dispatch trained, certified crews, equipment and inspection tools specializing in water damage. With our national footprint and large coverage areas throughout the country we will arrive on site and begin work quickly, minimizing the damage to your home. 

I spent a lot of time reading all these posts and frankly I can’t believe the way some people think. 1. If there is dust and dirt of any kind in my HVAC system I want it out, the mentality that it can stay there and it’s fine is fulish as the system turns on and off microscopic particulates will move in and out of your living space and you will definitely breath them in. The air quality of your home or office will only be as clean as the system that produces it. We don’t not clean things simply because we can’t see them, it’s what we can’t see that can do the most harm. Dust will build up in a system fairly quickly and will get damp at times allowing mold to grow and mold releases spores without any movement as part of its defense meconisam so don’t tell me that when your system turns on it won’t blow the spores out into the living spaces of your home. A build up of dust will cause failures to your system over time, equipment that works harder to do its job will run hotter with more strain and this will lead to brake downs and until then the system will run less efficient then it should. The system was engineered to move a certain volume of air through a specific duct size, when that duct size starts to become narowed down with dust build up your system has to work harder to move that air this is why you will end up with a loss of efficiency and eventually breakdowns or failures. I have seen systems develop a significant amount of dust build up in as little as two years, just look at how fast the filter gets clogged up and it isn’t all that hard to believe. As for all the scams that are out there they hurt the industry because people can’t decipher between them and the legitimate companies, BBB is helpful. Recommendations from HVAC contractors will be a good resource and a good company will provide a written estimate with a complete brake down of what they are going to do and why, most of which is comen sence once they explain it to you, then if you spend about 5 minutes watching them once they are set up you can see they are doing what they said they would do and let’s get real would you do a job that should take approx 3 hours per system for $29/$39/59 or something close to that, if you think you are going to get a good job from a comp that has to make money at that price you shouldn’t be mad at anyone but your self for trying to get quality work at a scam price. If it’s done right it will be very beneficial and depending on the size of your system and where you are in the world it’s going to cost you approx $300 to $600 per system large and or older systems may cost even more. Remember a quality job isn’t wasting money but a lousy job is, even if it’s only $29. I’d rather spend $600 on a quality job then $29 on a lousy job!! Good luck..
I hired duct cleaning company out of "Service Magic" website. I did not realize the name of his company was Duck cleaning of Central Florida...that should have given me a hint.. The guy did a very poor, incomplete job, and ruined a closet full of clothes when he sprayed up to clean a vent instead of taking it down and cleaning it outside. He left me with more than 1/2 dirty vents and ducts, did not do the air handler in the garage and failed to fog the system. He spent 6 useless hours at my residence and now his insurance is denying coverage..very disappointed in Service Magic....
You should be aware that although a substance may look like mold, a positive determination of whether it is mold or not can be made only by an expert and may require laboratory analysis for final confirmation. For about $50, some microbiology laboratories can tell you whether a sample sent to them on a clear strip of sticky household tape is mold or simply a substance that resembles it.
×