All these pro duct cleaners answer with "it's common sense, everything operates better when cleaner" etc. But your explanation is correct. Especially so with flex tube ducting where dust gets "stuck" between the lowest valleys (between wire coil supports) where air flow is drastically reduced -- which is more than 50 pct of the entire interior surface area of the flex ducting. That sounds like a bad thing but also has a good effect of trapping dust from escaping.
I noticed a lot of negative feedback, though unfortunately there are many dishonest companies out there. I currently work with a company that cleans duct work and we DO NOT use any scare tactics or up sell services or equipment. Once every 10years of course there are exceptions. We clean supply, returns, air handler, housing, motor, and fan. Though be discerning when qualifying anyone to work in your home. I would ask for REAL REFERENCES to contact.

He proceeded to clean each heat register by removing the grille and blasting it with an air pressure hose toward the duct opening thinking that the dust would magically be sucked inside. In one room this caused a ceiling smoke detector to go off because the excess dust fooled it into thinking there was smoke. I put my hand in front of a register he wasn’t working on and could hardly feel a suction. Although we discussed how I open and close damper doors, I realized later that he never checked, opened or adjusted them during the cleaning. He could have closed all but the one he was working on in order to increase suction results. His next step was to blast air into the duct and then attach a “squid-like” device that slapped around inside the duct as far as he could reach. This is important! In a newer house, ducts have long straight runs from the furnace. In older houses like mine they can turn and twist. In fact, the duct we have a problem with runs straight up from the basement inside a wall and turns 90 degrees into a soffit for three feet then into two 90 degree turns to get into the floor joist area for another two feet and finally a 90 degree turn up to the second floor register. When he cleaned this one he could only get three feet into the register with the hose or squid because of the turns. That was the case with most. Hardly what could be described as a decent cleaning.
Preventing against air leakage is great, but the only way to keep dust and debris out of a duct system would be to completely seal off the return-air side of the system, which would render the system useless. Cold-air returns will always pull dust and other particles into the system. A high-MERV rated filter is definitely a good idea, but it does nothing to keep the return side of the system clean. Definitely agree though to use foil tape to seal seams, etc. Duct tape dries out over time and as it does can actually add more particles to the air.
Very interesting article. I searched articles about services for cleaning ventilation systems. But I have some questions. For cleaning ventilation system used special products for cleaning. Can I know in company manager about, which type of cleaning products they use? Your family members may be allergic in some components. It’s very big problem. And one more problem it’s how to choose the right company in Internet. Sometimes I don’t have much time to find a company in my town and I use the Internet. But I find a lot of company. It is very popular services, for example, Stanley Steemer – https://www.stanleysteemer.com/ or my local not very popular service, for example, AllstatesAirDuctPro – http://allstatesairductpro.us/. Can I understand the company is professional or not, only looking through the website? What must I check on the website? Who has helpful information? I will very grateful for your help. Links I add for understanding my problem. They are random and not for advertising.
All of you have dentists, you have doctors, you have preachers, you have mechanics. You don’t have to know everything about everything but you have to have people in your life that you can trust. Don’t just open up the phone book and pick a mechanical (HVAC) contractor. Call your friends and family and ask for referrals. There are no black and white (scam or not a scam) answers here.
I am NADCA Certified Air Systems Cleaning Specialist. Over the years I have learned on simple answer to this questions: there air duct cleaners and there are pretenders. There will be no benefit at all if you use on the very cheap pretender because they will not really clean anything. On the other hand if you call a qualified air duct cleaner with a NADCA Certification you will, like 99% of my customers, report improvement with your respiratory problems, you will see less dust and the job will pay for itself with energy savings and repair prevention.
I always get a laugh at anyone claiming to be in the business for any length of time that doesnt understand the importance of cleaning out a ventilation system. Not only for better indoor air quality but for maintaining your heating equipment. I guess it makes more sense to some people that the furnace will just run better with a ton of dust and debris and maybe this wont be a big cause of sytem breakdown and malfunction. I mean really? Maybe this guy got a bad company and or cleaning and is a little jaded but to advise cleaning your grills , which does nothing, and replacing a filter....come on guy.
Manufacturers of products marketed to coat and encapsulate duct surfaces claim that these sealants prevent dust and dirt particles inside air ducts from being released into the air. As with biocides, a sealant is often applied by spraying it into the operating duct system. Laboratory tests indicate that materials introduced in this manner tend not to completely coat the duct surface. Application of sealants may also affect the acoustical (noise) and fire retarding characteristics of fiber glass lined or constructed ducts and may invalidate the manufacturer's warranty.

One of the best ways to know if your ducts or vents need to be cleaned is to just check them. Your eyes will be able to check for indications of mold, dust or pollen buildup. You might also be able to smell the presence of mold, which would be a clear indicator. Ductwork will have some buildup of dust, since the return registrars pull air back in. However, this doesn't mean your ducts have too much debris, and you can easily clean them with a duster or vacuum.


In reading through all this about duct cleaning, THE ONE preventative measure people need to realize is that a poorly installed HVAC system that is not sealed and air tight to ensure that ALL indoor air passes through a GOOD air filtration system IS THE best means of ensuring your ducts remain clean. Duct cleaning does not now and will NEVER improve an HVAC systems efficiency. Proper maintenance and installation are the key just as improper installation practices allow for dust infiltration into the duct system. I am a state licensed contractor in Texas, and unless people have their hvac system sealed and/or properly installed, duct cleaning is an absolute waste of money. My duct system is 12 years old as is as clean today as the day I installed the system with ductwork. SO before ANYONE jumps on the bandwagon of duct cleaning, get with your hvac professional FIRST.
Although i love to burn candles, depending on the type your asking for problems big ones! At work one day i had been talking with co workers about these black shadows that were appearing on my ceilings and higher wall areas. They seemed to in the corners and along the stud supports , i could even see what i thought to be where all had been nailed. There would be dark shadows perfectly straight across my ceiling and then real dark circels every few inches within the lines. I thought it was the propane heat but learned quickly that oil heat will do that but not normally propane. A co worker brought me a magazine with a huge article about candles and what actually burns off them when lit, an ashy soot that is attracted to the areas on walls and ceilings that omit the most heat or warmth, of course where the drywall and studs meet and corners of the room. Its been about 8 years since i painted the entire house. I started bending to my love for candles again in the last 3 years, surprise i will be spending part of my summer re painting again!! No more candles ,well maybe at the holidays LOL
As a homeowner and an owner of rental property I can tell you that the air ducts sometimes need to be cleaned. If you have had pets or anyone smoking in your home (even a visitor) for any length of time, having the ducts cleaned is really good idea. I had a tenant who did not smoke, but got married to a smoker more than year after moving in. When I realized someone was smoking I had them move out, but the smell was awful. I had the ducts cleaned and sanitized (it was a bit extra). The ducts were shiny like new afterwards. I left the windows open for a few days and we cleaned the place super clean and then replaced the carpets. The duct cleaning was worth every penny because the house looked, smelled, and felt new afterward. I plan to have my own house ducts cleaned again this year as we have two cats. We had them cleaned about 12 years ago and they found building materials in the ducts! If you move into a house that has never had them cleaned, it is good to do it. If you have allergies, clean the ducts to see if it helps. You never know what is in your ducts if you have never had them cleaned.
I believe a $3 [sic] pleated cotton filter is all that is ever needed to keep a system running top notch. A cleaning of the blower squirrel cage and of the evaporator [indoor] coil may be needed one time if fiberglass or no filters have been previously used. The return air grille [or grilles] need vacuumed off occasionally, as they are upstream from the filter. The $3 filter should be changed every 3 months [rule of thumb]....and most of them have a little white square on the cardboard frame to write install date.....and the arrow should point into the duct [if at filter grille]....or towards the furnace [if in ductwork slot]...or towards the blower [if in blower compartment]. My two cents.....
Pay particular attention to cooling coils, which are designed to remove water from the air and can be a major source of moisture contamination of the system that can lead to mold growth. Make sure the condensate pan drains properly. The presence of substantial standing water and/or debris indicates a problem requiring immediate attention. Check any insulation near cooling coils for wet spots.
Hi guys if your not convinced yet that duct cleaning is a waste of time. I’m a HVAC business owner install heaters and air conditioners. Simple facts if you have an old system get a new return air fitted with a filter it will catch all the dirt and dust. If you still have as many do black flecks and stuff coming through it is the lining inside your ducting that has perished. So somewhere you have a hole or very old ducting. If you had rats etc its a hole somewhere. To clean, stick your vacuum in the outlet and push the hose as far as it will go this gets 99% of toys and coins fur and alike. Think about it if the object is not heavy it will come out the duct when unit is on. Service the heaters or air con units but not the ducting. I would go further to say that duct cleaning actually damages the ducting in my opinion.
The most effective way to clean air ducts and ventilation systems is to employ Source Removal methods of cleaning. This requires a contractor to place the system under negative pressure, through the use of a specialized, powerful vacuum. While the vacuum draws air through the system, devices are inserted into the ducts to dislodge any debris that might be stuck to interior surfaces. The debris can then travel down the ducts to the vacuum, which removes it from the system and the home.
I spent a lot of time reading all these posts and frankly I can’t believe the way some people think. 1. If there is dust and dirt of any kind in my HVAC system I want it out, the mentality that it can stay there and it’s fine is fulish as the system turns on and off microscopic particulates will move in and out of your living space and you will definitely breath them in. The air quality of your home or office will only be as clean as the system that produces it. We don’t not clean things simply because we can’t see them, it’s what we can’t see that can do the most harm. Dust will build up in a system fairly quickly and will get damp at times allowing mold to grow and mold releases spores without any movement as part of its defense meconisam so don’t tell me that when your system turns on it won’t blow the spores out into the living spaces of your home. A build up of dust will cause failures to your system over time, equipment that works harder to do its job will run hotter with more strain and this will lead to brake downs and until then the system will run less efficient then it should. The system was engineered to move a certain volume of air through a specific duct size, when that duct size starts to become narowed down with dust build up your system has to work harder to move that air this is why you will end up with a loss of efficiency and eventually breakdowns or failures. I have seen systems develop a significant amount of dust build up in as little as two years, just look at how fast the filter gets clogged up and it isn’t all that hard to believe. As for all the scams that are out there they hurt the industry because people can’t decipher between them and the legitimate companies, BBB is helpful. Recommendations from HVAC contractors will be a good resource and a good company will provide a written estimate with a complete brake down of what they are going to do and why, most of which is comen sence once they explain it to you, then if you spend about 5 minutes watching them once they are set up you can see they are doing what they said they would do and let’s get real would you do a job that should take approx 3 hours per system for $29/$39/59 or something close to that, if you think you are going to get a good job from a comp that has to make money at that price you shouldn’t be mad at anyone but your self for trying to get quality work at a scam price. If it’s done right it will be very beneficial and depending on the size of your system and where you are in the world it’s going to cost you approx $300 to $600 per system large and or older systems may cost even more. Remember a quality job isn’t wasting money but a lousy job is, even if it’s only $29. I’d rather spend $600 on a quality job then $29 on a lousy job!! Good luck..
I noticed a lot of negative feedback, though unfortunately there are many dishonest companies out there. I currently work with a company that cleans duct work and we DO NOT use any scare tactics or up sell services or equipment. Once every 10years of course there are exceptions. We clean supply, returns, air handler, housing, motor, and fan. Though be discerning when qualifying anyone to work in your home. I would ask for REAL REFERENCES to contact.
#3 The ONLY time Duct cleaning is needed is when the home had a fire, Bad roof leak on to FIBERGLASS ductwork or house sat vacant for many years with out the air running. And its better to replace than to do “abrasive” duct cleaning. If the duct cleaning has a rotating brush it will remove part of the glue that is holding the Fiberglass in the ducts together, PERIOD no matter how much the say it don’t because the brush is soft.
I purchased one of those Amazon air duct cleaning coupons for 49.99. When the company showed up, they removed the vent closest to the air intake and immediately told me I needed $1800.00 for all new duct work. They said they could not clean the system until new duct work was installed. I thanked them and said I would give them a call. The only call I made was to Amazon to get a refund. I know I didn’t need new duct work. Be careful to not fall for unscrupulous salesmen and their pitches and scare tactics.
I own an HVAC company. Dirt in your ducts stays there and hurts no one. It is like dirt on the ground outside. This industry was infiltrated by a bunch of money grubbing low lifes years ago. As a credible company, we do not clean air ducts. Some who were credible probably signed on not knowing what else to do or to try to make a buck another way. These companies, because they also do HVAC work not only rip off private homeowners, they are ripping off legitimate HVAC company's customers and the integrity of what can and should as a rule be a great service industry. Some probably have gotten into this to simply offer what competitors who were ripping off their customers were offering. Anyone cleaning ducts is in my opinion raising a big red flag that they cannot and should not be trusted. Political pressure from NADCA, advertising dollars, manufacturers and marketers of duct cleaning equipment, and intense competition for the customers is the only reason the government and adverstising companies have not run them out of business and that this cancer perpetuates itself.
I guess I should present my credentials first, I am a 30 year veteran of the heating and cooling industry. I started at the bottom and have participated in every area of the trade. Installer, service, maint. Ownership, rep, territory manager and so on. A forced air duct system is a large vacume. Like your vacume it has an air intake (return air) and an exhaust (supply registers). A filter just like a vacume (located next to furnace or air handler). Now I want you to visualize something. Put your head inside your vacume cleaner and breath. Get the picture? This is what your duct work looks like. Do you clean your vacume when it’s dirty? If it’s full and the filter is dirty you lose performance and it starts poluting the air you breathe. It’s common sense. I recommend hiring a duct cleaning outfit that you have researched to be honest, background checked, drug tested, insured, and highly recommended by your piers in the area. The service is a necessity, but like everything, it should be done by a qualified company.
I have been a plumbing/gas/hvac tech for 19 years, before that I installed ductwork in commercial buildings and office towers. As the article states, unless you have undergone some type of extensive reno, or ducts have become contaminated, paying for cleaning is pointless. Its one thing if you have a 30 year old home that has never had a duct cleaning and you can actually see mounds of dust built up , especially in the return side, then go for it. Keep in mind that most duct cleaning companies will only get 80% of the dust , or less at best. Keep in mind that most of the dust in your home is lint from clothes and linens, and skin cells from you and your pets and is constantly being generated. Dust that builds up in ductwork , generally stays in the ductwork. The power of suggestion, scare tactics, up sell!!!
I agree that good filtration and a sealed system will prevent the need for duct cleaning. However, when we do get called it is because the duct work has reached a noticeable state of restriction or dust or the homeowner is hyper-sensitive to these pollutants in their home. Most of the time we find that no filter or a cheap (99 cent) filter is being used or they have serious duct leaks in the system. If you are hiring a cleaner make sure they are using professional cleaning equipment which will consist of a rotating brush system and a vacuum source. Be highly skeptical of the contractor with no branded system or the guy who shows up with just chimney brushes and a shop vac. He will not be able to reach around all the corners or all the runs in your system and he will be taking your money for a superficial cleaning at best. Only trust a company that offers VIDEO inspection and more importantly.... a contractor who repairs, installs and seals ducts if a problem is discovered or heaven forbid, created. Good luck and get your ducts sealed if you do have a leak! It is one of the greatest energy losses to a home other than being poorly insulated.
When these aren't properly maintained and sanitized, they can build up dust, pollen, and even mold. This means when the air conditioner or heater turns on, the spores are released into the air for you to inhale. While some are less harmful, people who have allergies or sensitivity to certain spores will react negatively. Plus, mold is dangerous for anyone to ingest and should be avoided by regular maintenance.

I own and live in a mobile home and was told to install a mobile home air condition well I did not want one because the ones for moblie homes are to small,so I install a home air-condidtion and its good for heating and cooling the only thing I do is change is the filter every month or two,What I want to know is how does dirt and dust comes from????

You and your family spend hours sitting on your favorite chairs, couches and sectionals. Over time, dander and body oil become trapped in the upholstery, but with regular cleanings you can keep these delicate fabrics looking, feeling and smelling great. We examine your furniture and select the best process to safely clean and protect any kind of upholstery, including leather. 

You may consider having your air ducts cleaned simply because it seems logical that air ducts will get dirty over time and should be occasionally cleaned. Provided that the cleaning is done properly, no evidence suggests that such cleaning would be detrimental. EPA does not recommend that the air ducts be cleaned routinely, but only as needed. EPA does, however, recommend that if you have a fuel burning furnace, stove or fireplace, they be inspected for proper functioning and serviced before each heating season to protect against carbon monoxide poisoning.

×