Moisture can enter the duct system through leaks or if the system has been improperly installed or serviced. Research suggests that condensation (which occurs when a surface temperature is lower than the dew point temperature of the surrounding air) on or near cooling coils of air conditioning units is a major factor in moisture contamination of the system. The presence of condensation or high relative humidity is an important indicator of the potential for mold growth on any type of duct. Controlling moisture can often be difficult, but here are some steps you can take:
Had duct cleaned (apartment) however, dust is still settling throughout the apartment. Contractor said no other cleaning necessary until two (2) years. Is there a time period before dust no longer settles prior to that time? Should the vendor had worn a mask? He did not cover his face the vents and dust was blown throughout the apartment (had family help with the cleanup). I had to leave when they left because I have asthma and I couldn’t breathe without coughing. Please help!
Hi guys if your not convinced yet that duct cleaning is a waste of time. I’m a HVAC business owner install heaters and air conditioners. Simple facts if you have an old system get a new return air fitted with a filter it will catch all the dirt and dust. If you still have as many do black flecks and stuff coming through it is the lining inside your ducting that has perished. So somewhere you have a hole or very old ducting. If you had rats etc its a hole somewhere. To clean, stick your vacuum in the outlet and push the hose as far as it will go this gets 99% of toys and coins fur and alike. Think about it if the object is not heavy it will come out the duct when unit is on. Service the heaters or air con units but not the ducting. I would go further to say that duct cleaning actually damages the ducting in my opinion.

There are many interesting comments from several informed individuals. The question that has not been answered is how do duct systems get dusty and dirty? As a RESNET Home Energy Rater, I perform pressure tests on homes and duct systems, and the one common thread is . . . most air delivery sytems have large amounts of air leakage. The solution is to seal the duct system, and pay particular attention to the return duct system and ductwork near the air handler (the 'blower'). As others have said, a captive (sealed) duct system with proper filter maintenance should be more then adequate for most occupants. For those who have allergy, asthma, or other breathing problems, a filter with a higher MERV rating (number should be listed on the package) or a HEPA filter are good choices. These filters will capture smaller particulates and should improve the indoor air quality. Again, make certain that the entire duct system is sealed, preferably with mastic, second choice UL-181 foil tape - never use cloth duct (also known as duck) tape.


One of the best ways to know if your ducts or vents need to be cleaned is to just check them. Your eyes will be able to check for indications of mold, dust or pollen buildup. You might also be able to smell the presence of mold, which would be a clear indicator. Ductwork will have some buildup of dust, since the return registrars pull air back in. However, this doesn't mean your ducts have too much debris, and you can easily clean them with a duster or vacuum.

If you want to get some of the dust and debris out of your ventilation system, you can mix household cleaners like bleach with water, dip a cloth in the mix and then the wipe out the system. This will remove a layer of the spores, which could increase the quality of air a bit and help with the flow of air throughout the house until a pro can come out.


#3 The ONLY time Duct cleaning is needed is when the home had a fire, Bad roof leak on to FIBERGLASS ductwork or house sat vacant for many years with out the air running. And its better to replace than to do “abrasive” duct cleaning. If the duct cleaning has a rotating brush it will remove part of the glue that is holding the Fiberglass in the ducts together, PERIOD no matter how much the say it don’t because the brush is soft.
yes get a good company and pay the price, I found so much dust and dirt and wood and paint chips and bugs and even bottle caps in my ductwork. I hired a major plumbing company who cleaned ductwork and i will say they did an excellent job cleaning my vent. they did miss one point in my ductwork because i still started to see dust all over my furniture and i realized that my retunduct work that was connected with a piece of sheet metal beam which was 16" across , the contractor that built my condo used a 16" wide sheet of sheet metal to connect the vent system to my return for the air to return back into my condo. The contractor should have built a 8" x16" square duct by 6 feet long to connect my intake to my return instead of using a sheet of sheet metal 16" wide by using two 3' sections by 16 inches wide. That was a shor cut which caused a major problem fir me.
i got angies list deal for 109 air duct clenaing, dryer vent cleaning, and furnace inspection, {healthy duct cleaning} i call the company, they arrive on time. did excellent service what ever i purches i got. they give me furnace inspection and the told me that my furnace is very dirty and they offer me to clean that for 250 extra. i paid and i am very happy from this service. i try before 2 diffrent company that i got deal from them as well the just give me estimate and don’t even do the job. so guys don’t spend time if you need deep cleaning just cal this guy the offer free estimate as well.

I've been in business in Florida for 25 years and purchased a $12,000 duct cleaning system 4 years ago. In the last four years I've cleaned 5 duct systems charging around $400 each. Not a very good return on investment. What I have been doing most the time is I get a call by someone panicked because they called some low priced company to inspect their system and were told they have dangerous black mold. Then they call me to have a look. Most the time they don't have mold, ducts look very clean. However the coils are dirty and the inside of the air handler cabinet needs cleaning. Keep in mind not every system can handle supper high efficiency filters! These filters can block air flow quite a bit right out of the package. Many older systems can't handle pleated filters due to increased static pressure. "Back rooms with low air flow". I have taken many hours of classroom study on indoor air quality. Never got any certification because I don't want to pay another organization dues yearly. I think the problem with duct / system cleaning is most people are suckers for low priced scams that are rip- offs . People call me all the time and ask how much? When I tell them average $400 they hang up. I know I do the job correctly and honestly, and they are going to get racked over the coals by the scam artists by calling $79 whole house duct cleaning guys. People need to check internet, angies list and BBB reviews. But keep in mind even reviews need to be sifted through your rational person filter.


NADCA and EPA both have good points. Although, organizations are made to make money. Common sense and looking at NADCA and EPA pre-checklist. If you don't see it in the check list, you don't have to do it! But, if you do, look up Diamond certified co.s and the BBB. Beware of bait and switch scams, $60 vents and the like coupons which claim to help all for the measley sum of $79.00 bucks.

yes get a good company and pay the price, I found so much dust and dirt and wood and paint chips and bugs and even bottle caps in my ductwork. I hired a major plumbing company who cleaned ductwork and i will say they did an excellent job cleaning my vent. they did miss one point in my ductwork because i still started to see dust all over my furniture and i realized that my retunduct work that was connected with a piece of sheet metal beam which was 16" across , the contractor that built my condo used a 16" wide sheet of sheet metal to connect the vent system to my return for the air to return back into my condo. The contractor should have built a 8" x16" square duct by 6 feet long to connect my intake to my return instead of using a sheet of sheet metal 16" wide by using two 3' sections by 16 inches wide. That was a shor cut which caused a major problem fir me.


fact is most homes have bad filter racks. when you insert the filter it doesn’t seal well to the sides so some of the air and dust bypass it and end up in the supply ductwork and into the house. Most of the dust in the supply ductwork settles down and doesn’t get blown in the house but some of it does when the blower starts up or when you put a new filter. If you have allergies or other health problems put in an electronic air cleaner, get your ducts cleaned and run the fan as much as you can afford. you can also get an ECM motor installed which is going to be worth it if you want to run the fan 24/7. If you have uninsulated metal ducts take down the ones you can and wash them. Then put them back and seal the joints. Cleaning the ductwork also improves airflow which is important to AC and Heat pump systems for efficiency. An electronic air cleaner will also improve airflow and static pressure because they usually have a much larger filter surface area. An electronic air cleaner also keeps the ac coil clean like new which means better efficiency and no cleaning needed. AC furnaces sometimes grow mold around the coil because of the condensation. Electronic air cleaners should be able to filter mold spores but the best remedy is installing a UV light next to the coil which will kill the mold.
Is duct cleaning worth it? There is not a yes or no answer that suits everyone. On an Air Force base, the system was not air tight and there was leakage around the filters. The system got dirty. A professional company was called out. The Duct was big enough that a technician could go inside the metal duct and clean it. There was a new Air Handler installed and things were sealed up better. in this case it was worth it.
If the system is sealed air-tight and a really good filtering system is in place then you should NEVER have to clean your ductwork. Most dust people see in their homes (on beds furniture etc....) is broken down insulation that is being blown into the home from the attic (venturi effect) where the duct bucket (box etc...) is not sealed at the sheetrock ceiling. On the return side, ANY leaks in the ductwork will pull hot attic air and dust into the system, clogging up everything.
The Antimicrobials Information Hotline provides answers to questions concerning current antimicrobial issues (disinfectants, fungicides, others) regulated by the pesticide law, rules and regulations. These cover interpretation laws, rules and regulations, and registration and re-registration of antimicrobial chemicals and products. The Hotline also provide information health & safety issues on registered antimicrobial products, product label and the proper and safe use of these antimicrobial products.
I purchased a Groupon for cleaning of unlimited air ducts and one return vent for $39. I should have checked into their hours first because they only offer services during normal business hours. So, with no evenings or weekends available you have to take time off work. I asked Groupon for a refund when I realized this and they refused because it wasn’t within the three day window. Then they didn’t even show up or call for the appointment. I called them after they were an hour late and they were going to call the local dispatch office and have them call me back within 15 minutes. I did not receive that call. I called again and was told I would get a call back from a manager. That didn’t happen either. So I asked Groupon for a refund again and they gave me Groupon bucks. When the survey came asking if I was satisfied with the Groupon customer service I said no, I want real money. I got my real refund the next day. Seems to me Groupon should stop dealing with these companies.

I own and live in a mobile home and was told to install a mobile home air condition well I did not want one because the ones for moblie homes are to small,so I install a home air-condidtion and its good for heating and cooling the only thing I do is change is the filter every month or two,What I want to know is how does dirt and dust comes from????
HELP is am drowing in LENT . It has been noticed in the master bedroom there is lent all over the furniture and the floors. I have dark brown/black furniture and same for the wooden floors. There are wods of lent every day. My furniture covered in lent. The rest of the house is fine just the tipical dust. I am sure my lungs are also full of lent. I looks like if my dryer vent was in my bedroom. Please help
2. If air quality is so important and duct cleaniliness is so uncertain, why not adopt doubling filtering; that is, in addition to the existing main furnace filter, add a filter at each air outlet. I understand replacing so many filters would be a burden, but air outlets can be designed for easy filter replacement. The builders and home design engineers should bear responsibility to provide good and low maintenance homes, rather than prioritizing on fancy or costly featuers for homes.

I have worked cleaning HVAC in my area for almost 5 years. I always do a thorough inspection and cleaning, providing before and after photos. I have completed some jobs where I felt that it was not entirely necessary, but ultimately what the customer wanted. With that being said, I have endless photos of unspeakable horrors. Hotels are usually nasty, post construction mess is certain, pets and kids create lots off debris, bugs congregate and die, then spiders set up and die, I have even had one supply that was nearly plugged with sand!
i got angies list deal for 109 air duct clenaing, dryer vent cleaning, and furnace inspection, {healthy duct cleaning} i call the company, they arrive on time. did excellent service what ever i purches i got. they give me furnace inspection and the told me that my furnace is very dirty and they offer me to clean that for 250 extra. i paid and i am very happy from this service. i try before 2 diffrent company that i got deal from them as well the just give me estimate and don’t even do the job. so guys don’t spend time if you need deep cleaning just cal this guy the offer free estimate as well.

The answer to your question is most likely "Yes," but not defiitely. It depends on where the dust is coming from. Now, if your house is more than say, 12 years old then you likely do have leaks in your ducts that can let in insulation particles and dust from your attic. If this is the case then cleaning of the ducts-PROPER CLEANING, which like the article sas doess include EVERYTHING that the conditioned air passes through, such as your indoor evaporator coil and blower housing assembly-is definitely a good first step to getting that dust under control! Of course I highly recommend that you also have your ducts SEALED as well, or else you will have to repeat the cleaning some time down the line. As a 3rd step, consider an electronic air filter. I always thought they were a scam, personally, so I never bothered selling them to my clients. Then one day my manager sent me to install one for a senior couple in a mobile home. The wife had bad allergies, and her eyes were constantly watering and puffy and red. Well, I did a quality check 60 days later and she could not stop praising that air filter! Keep in mind that in a mobile home, duct seals are not as complete as those in other homes due to access issues.


Maybe I took him to literally but I am pretty sure cops wont show up to ensure that my duct gets replaced. He said it would be over 1000 dollars to replace the ductwork if that is the case. Now, I spoke to a friend who did 2 ductwork lines on his own in his attic and he said it was like 15 dollars for the plastic wirewound tubing to create new ducts. Should I cancel that appointment and just do the work on my own? I feel like I’m a chump or lazy for considering paying someone to do this work.
We are all getting migraines several times a month. I have asthma but not ever as bad as it has been and my 2 year olds dr just informed me she potentially has asthma too. We all get sinus infections regularly and eczema and contact dermatitis. None of us have been this way until recently in our apartment. A roof leak with mold was repaired recently mold was sealed off not removed. We also had lead paint removed from a few window trims this year. I wasn’t here to see if they covered the vents. We had mice too. I vacuum everyday we have hardwood floors no one wears shoes past the font door and I’m getting over a cup full of dirt every time I vacuum. Dust on everything daily. White dust. It’s a 4 room apartment with 1 intake. They are filthy from what I can see when I change the filters. The filters are black after a few months. I feel bad to ask the homeowner to get the system cleaned, can’t afford to move (we live in the city & it’s expensive). I am going to try the shop vac to remove what I can. Any experienced hvac people please give your opinion. Should I just get it done and pay for it myself? We have lived here for 13 years. It’s never been cleaned since ive been here. Is it something I can do with a shop vac? Can i use a wet rag to get the powder dust on the inside of the vents off. One vent has what looks like chunks of dry wall or thick paint sitting in the vent and none of the vents screw into the wall, the screws just fall out. No one ever reinforced the area so the wall just basically crumbles. Kind of useless to spend the money on filters since the air and dust just blows out around the sides of the vents and one of the vents just falls right out of the wall when the heat is turned on. I don’t know why the owner doesn’t fix it. He’s been here to replace filters and saw the condition.

If not properly installed, maintained and operated, these components may become contaminated with particles of dust, pollen or other debris. If moisture is present, the potential for microbiological growth (e.g., mold) is increased and spores from such growth may be released into the home's living space. Some of these contaminants may cause allergic reactions or other symptoms in people if they are exposed to them. If you decide to have your heating and cooling system cleaned, it is important to make sure the service provider agrees to clean all components of the system and is qualified to do so. Failure to clean a component of a contaminated system can result in re-contamination of the entire system, thus negating any potential benefits. Methods of duct cleaning vary, although standards have been established by industry associations concerned with air duct cleaning. Typically, a service provider will use specialized tools to dislodge dirt and other debris in ducts, then vacuum them out with a high-powered vacuum cleaner.
×