How exactly do you expect to kill or remove mold without it ? You can’t even clean your hvac systems coils without moisture of some type ,if you use a steam cleaner you can literally clean the whole system minus the electronics . You should do more research and possibly talk to people who do the work before posting , but don’t listen to me i only have a class A contractor license ,epa license , install /repair hvacs , rent and flip houses for a living .
Sounds like your first hvac company was ripping you off. Ask your new company to go to your coil and see if there is a leak. If there isn't the last company was just lining their pockets. If you have had ducts unhooked for a long time I would recommend duct cleaning, trust me I'm not a fan of duct cleaning myself. I have done hvac for 20 yrs. in GA. When I just bought a home built in 1996, we had all the ducts replaced immediately.
I called a company name “GREEN RHVAC” with their $29.00 one system air duck cleaning. When the guy came with a truck I asked him to tell me how much he will charge and he said that if he gave me price and I didn’t want the service then he would charge me $89 or he would tell me how much he charge me after he finished the work. I immoderately sense that I made mistake to call him to my house. To cut my lost I asked him to give me the price and it was $1600 for two systems house. I paid $100 to him for my lesson to learn and search online to find this site is very helpfully and I should do it before to call anyone for air duck cleaning.
In addition, the black dust was found in most of the heat registers. He could rub it off on his fingers but did nothing but spray compressed air on it which didn’t make it disappear since it wasn’t loose. Also, in the register in the basement he described the black dust as being oily. The reality of that situation is that I had the AC on until the morning of the service and minutes after he snaked the hoses in my back door it started raining. The basement register had condensation from the humidity all over it. It was not oily but wet. He asked for an old towel and wiped it out. Never saw anything so black – because I never had to clean soot. That is what I have in my ducts. Soot from years of the old coal furnace.
There is a lot of good, general information in the article. As with anything, the homeowner should do their due diligence in getting enough information to make an educated decision. Should duct-work be cleaned? YES! Does it need to be cleaned annually or even every second or third year? Not necessarily. It all depends on a bunch of variables. You're right that a well designed and balanced system will deliver the right amount of air flow, but sometimes conditions outside the home/business, make it a necessity to get the ducts cleaned. As for mold? NO filter is going to address a mold issue. If you have mold, you have a moisture issue that needs to be addressed. Also, in my 38 years of experience in the HVAC and sheet metal industries, washable filters are one of the reasons ducts need to be cleaned. They are no where near efficient in cleaning/filtering the air to the level that they should.

I have lived in Calgary for quite some time now. When I first moved here I couldn’t stand the humidity levels. Its like a desert come winter. When I first moved into my new home, the house inspector insisted I have my furnace and ducts cleaned. I was very sceptical about duct cleaning to begin with. The company I hired came on time and were very respectable from the start. Before mentioning anything they asked me what my concerns were and what issues I was having. They were more concerned about addressing my issues then bringing anything non related up. I ended up going with this company and getting a humidifier installed a couple days later after the cleaning. Its been almost 4 years now that I have been here. The humidifier is working great and the difference is incredible. They took me around explained step by step what they were doing and the reasons they were doing it. With all those other companies out there, I am glad I found them at this site.
I have been a plumbing/gas/hvac tech for 19 years, before that I installed ductwork in commercial buildings and office towers. As the article states, unless you have undergone some type of extensive reno, or ducts have become contaminated, paying for cleaning is pointless. Its one thing if you have a 30 year old home that has never had a duct cleaning and you can actually see mounds of dust built up , especially in the return side, then go for it. Keep in mind that most duct cleaning companies will only get 80% of the dust , or less at best. Keep in mind that most of the dust in your home is lint from clothes and linens, and skin cells from you and your pets and is constantly being generated. Dust that builds up in ductwork , generally stays in the ductwork. The power of suggestion, scare tactics, up sell!!!
You and your family spend hours sitting on your favorite chairs, couches and sectionals. Over time, dander and body oil become trapped in the upholstery, but with regular cleanings you can keep these delicate fabrics looking, feeling and smelling great. We examine your furniture and select the best process to safely clean and protect any kind of upholstery, including leather. 
Maybe I took him to literally but I am pretty sure cops wont show up to ensure that my duct gets replaced. He said it would be over 1000 dollars to replace the ductwork if that is the case. Now, I spoke to a friend who did 2 ductwork lines on his own in his attic and he said it was like 15 dollars for the plastic wirewound tubing to create new ducts. Should I cancel that appointment and just do the work on my own? I feel like I’m a chump or lazy for considering paying someone to do this work.
NADCA and EPA both have good points. Although, organizations are made to make money. Common sense and looking at NADCA and EPA pre-checklist. If you don't see it in the check list, you don't have to do it! But, if you do, look up Diamond certified co.s and the BBB. Beware of bait and switch scams, $60 vents and the like coupons which claim to help all for the measley sum of $79.00 bucks.

Furnace cleaners are mostly young men, I know this, I have been one for 15 years or so……so heres the truth, if there are any allergies, children, older people with health issues, we are GOING to make money. do not tell the company you have hired about any health complication. they are salesmen. and they don’t care about you. or your money. make sure they do a good job, then kick them out. you don’t need all the bells and whistles they wanna sell you. any idiot can clean duct work, like I said, I am one of them. I am very good at it, but I don’t have the back bone to sell a widowed old lady a humidifier that she doesn’t need for 500 bucks, overall, if you think you need this service done, which you probably don’t, get it done, do not spend anything over 300$ and do not do it again for at least ten years.


No one has addressed mfg homes and doesn't seem any of the comments are from people in So CA which of course does make a difference as my dust comes from the outside not from the vents. My windows are open pretty much 365 days a year. Secondly mfg homes don't have basements or attics I keep mine clean with my vacuum as they are only about 2 ft deep. I purchased my home 10 yrs ago and it is a high end home but have never had a problem. I clean my furnace filter about twice a month as I have cats and most everything in there is cat fur. I am not saying they don't ever need to be cleaned but I am questioning mfg homes, I also clean my own filters in my AC unit outside as the HVAC guy told me too he QUATITY they would sell. I use this same company every year now for my tune up and inspection which takes them about 10 minutes. Not a bad return for them and I don't mind the $79 fee. If anyone has more info than this on mfg homes please let me know!


What about ringworm? If the fungus is as contagious as doctors warn, and the spores can live several months, doesn’t it make sense to spray some sort of fungus killer into the HVAC system to kill the spores that it has sucked in from the air? Duct cleaning would not be helpful at all here; these spores are microscopic and it could actually spread them further. But given how severely contagious ringworm is, body and especially scalp, does anyone make an aerosol product that will clean the system and kill the fungus? One the resident can use, not call an HVAC company; you can’t do that when you are in an apartment. I hear it’s not the same as mold, it is much more difficult. Truth?

I am NADCA Certified Air Systems Cleaning Specialist. Over the year I have learned on simple answer to this questions: there air duct cleaners and there are pretenders. There will be no benefit at all if you use on the very cheap pretender because they will not really clean anything. On the other hand if you call a qualified air duct cleaner with a NADCA Certification you will, like 99% of my customers, report improvement with your respiratory problems, you will see less dust and the job will pay for itself with energy savings and repair prevention.
I spent a lot of time reading all these posts and frankly I can’t believe the way some people think. 1. If there is dust and dirt of any kind in my HVAC system I want it out, the mentality that it can stay there and it’s fine is fulish as the system turns on and off microscopic particulates will move in and out of your living space and you will definitely breath them in. The air quality of your home or office will only be as clean as the system that produces it. We don’t not clean things simply because we can’t see them, it’s what we can’t see that can do the most harm. Dust will build up in a system fairly quickly and will get damp at times allowing mold to grow and mold releases spores without any movement as part of its defense meconisam so don’t tell me that when your system turns on it won’t blow the spores out into the living spaces of your home. A build up of dust will cause failures to your system over time, equipment that works harder to do its job will run hotter with more strain and this will lead to brake downs and until then the system will run less efficient then it should. The system was engineered to move a certain volume of air through a specific duct size, when that duct size starts to become narowed down with dust build up your system has to work harder to move that air this is why you will end up with a loss of efficiency and eventually breakdowns or failures. I have seen systems develop a significant amount of dust build up in as little as two years, just look at how fast the filter gets clogged up and it isn’t all that hard to believe. As for all the scams that are out there they hurt the industry because people can’t decipher between them and the legitimate companies, BBB is helpful. Recommendations from HVAC contractors will be a good resource and a good company will provide a written estimate with a complete brake down of what they are going to do and why, most of which is comen sence once they explain it to you, then if you spend about 5 minutes watching them once they are set up you can see they are doing what they said they would do and let’s get real would you do a job that should take approx 3 hours per system for $29/$39/59 or something close to that, if you think you are going to get a good job from a comp that has to make money at that price you shouldn’t be mad at anyone but your self for trying to get quality work at a scam price. If it’s done right it will be very beneficial and depending on the size of your system and where you are in the world it’s going to cost you approx $300 to $600 per system large and or older systems may cost even more. Remember a quality job isn’t wasting money but a lousy job is, even if it’s only $29. I’d rather spend $600 on a quality job then $29 on a lousy job!! Good luck..
While you consider having your air ducts cleaned, it is a good idea to take a look at your dryer vent. If your dryer vent is clogged, you could be losing energy efficiency. Worse yet, you could be increasing the risk of a house fire. Having your dryer vent professionally cared for costs about $130 on average, and could save you a bit of money and a lot of headaches in the future. For more information on the benefits and cost of having your dryer vent cleaned, take a look at our comprehensive cost guide.
I live in Port Orange, FL. I purchased a double wide mobile home and was saddened to learn that the previous owners were HEAVY smokers! They did a good job “hiding” the smoke smell the day we viewed this place. I did not have a home inspection done unfortunately. My question is: can duct cleaning remove the smoke smell from this place. The ceilings have been treated with Kilz and paint. I personally scrubbed down every wall, floor or surface. I also purchased a ODORFREE OZONE machine. It seemed to remove the odor for a short period of time but my friends are again complaining about the “smoke” odor in my home. The Ozone machine was $400 and I’m terribly upset that it didn’t clean the air as was promised.
WELL, this summer when I opened them up we had black dust spewing from one of the upstairs vents. It resembled the fuzz that comes off new towels. This prompted us to look into duct cleaning. We heard from someone who had it done several times, said it was worthwhile, and knew of a firm that did a good job. Clean Air America sent a single technician for the appointment and after counting registers and ducts gave me a price of $360.00 which included “sanitizing” the system (a $99 additional fee per can used). The small size of the plenum forced him to connect the 8” round vacuum hose from the truck to the 10” square opening from our humidifier unit. In hindsight, a mistake since it reduced the “negative” pressure in the system.
The most effective way to clean air ducts and ventilation systems is to employ Source Removal methods of cleaning. This requires a contractor to place the system under negative pressure, through the use of a specialized, powerful vacuum. While the vacuum draws air through the system, devices are inserted into the ducts to dislodge any debris that might be stuck to interior surfaces. The debris can then travel down the ducts to the vacuum, which removes it from the system and the home.

I recently did some remodeling and figured I’d get the air ducts cleaned in our 12 year old home. After obtaining 4 estimates between $572 and a whopping $3,075 for 25 vents and 2 air handlers, I knew I was in for a ride. I read through this blog and decided to use a $79 inspection camera I just found online (Home Depot) to take a look at all my ducts by removing the ceiling grilles first and then try to get into the ducts from the other end. From what I have just learned here, I believe that will take care of my “concerns”.
I recently replaced my 44 year old furnace. Over the years we have had several construction projects inside the home. For many years breathing the heated air from the duct work caused excessive sneezing, sinus issues, and lung irritation. . The heat smelled like dust. To maximize air quality I added a humidifier, MERV-11 filter, and UV light onto the new furnace. To further improve air quality, I had the ducts cleaned and sanitized. I took before and after pictures of the inside of each return and output duct. They were filthy before, and sparkling clean and fresh after the procedure. Now when running the system, clean sanitized air flows through my whole house. A huge difference. It will make sleeping and being indoors during the winter months far more tolerable. I use window air conditioners, and run the system in the summer to keep the house air clean and fresh on hot summer days too. It works! Great decision!
I've been in business in Florida for 25 years and purchased a $12,000 duct cleaning system 4 years ago. In the last four years I've cleaned 5 duct systems charging around $400 each. Not a very good return on investment. What I have been doing most the time is I get a call by someone panicked because they called some low priced company to inspect their system and were told they have dangerous black mold. Then they call me to have a look. Most the time they don't have mold, ducts look very clean. However the coils are dirty and the inside of the air handler cabinet needs cleaning. Keep in mind not every system can handle supper high efficiency filters! These filters can block air flow quite a bit right out of the package. Many older systems can't handle pleated filters due to increased static pressure. "Back rooms with low air flow". I have taken many hours of classroom study on indoor air quality. Never got any certification because I don't want to pay another organization dues yearly. I think the problem with duct / system cleaning is most people are suckers for low priced scams that are rip- offs . People call me all the time and ask how much? When I tell them average $400 they hang up. I know I do the job correctly and honestly, and they are going to get racked over the coals by the scam artists by calling $79 whole house duct cleaning guys. People need to check internet, angies list and BBB reviews. But keep in mind even reviews need to be sifted through your rational person filter.
While your HVAC filter is designed to trap particulate matter and prevent it from entering your air ducts, particles often still get through. The number of particles your HVAC filter traps is directly connected to the quality of air in your home: the lower the quality of air, the more particles will be present, and the more particles are likely to get through the filter. If these particles are allowed to build up, your HVAC system can become less efficient, operating longer to heat or cool your home. An inefficient HVAC system can result in inconsistent heating or cooling, higher utility costs, and expensive HVAC unit repairs, such as an A-coil or blower motor replacement if the problem is left unchecked. Air duct cleaning from Sears, which focuses on the dirt in your air ducts, can boost the efficiency of a dirty HVAC system, cleaning out the particulate matter that can hinder HVAC effectiveness and affect your health.
1. Ducts need cleaning mostly because they were not installed properly. There should be regulatory inpection and approval of clean and proper duct works on new houses. I was extremely unpset when I looked and found significant amounts of construction dust in parts of the ducts in my new house. There is apparently no way to hold the bullder to be responsible for clean ducts.
Duct cleaning is a band aid, like washing you hands is. Under your description, why wash your hands more than once? If it gets cleaned once, it shouldn't get dirty again. Well that is, unless they touch something dirty. Keeping your hands completely clean is virtually impossible. Same as keeping dust out of your home. You clean your ducts and over a 3-5 year span they get dirty again. Also, duct cleaners are not licensed but should be certified by NADCA(National Air Duct Cleaning Association).
The average cost of keeping your residential ductwork orderly is going to vary greatly from that of a commercial building. This is because commercial air ducts are often larger and more extensive. Residential cleanings can cost an average of about $20-$30 per vent. For commercial buildings, service providers must do an estimate of your space before they can provide an accurate quote. Before factoring in the materials and the number A/C and furnace units, you can expect a commercial project to cost at least $35-$50 per hour.
I read your article with interest and think it is a good start. One service that is always talked about is fogging ductwork for sanitizing. Many companies offer this service for disinfecting or adding a clean smell to the ductwork. Before any chemical or disinfectant is used, please read the MSDS (Material Safety Data Sheet). You might be surprise on what you are putting into the air stream. This is a high profit service and should be explored thoroughly before purchasing,
The original furnace was a coal fired “octopus” design which had no blower to circulate the air but relied upon warm air rising to distribute the heat. That also means that the system breathed air in from the basement and most of this type did not have a cold air return system. At some point (probably in the 1940’s) the system was upgraded to a forced air gas furnace. The upgrade included replacing the 12″ diameter air ducts exposed in the basement with 6″ ducts and a cold air return system of ducts from the two (only two) air returns on the first floor.
Having evaporator and condenser coils cleaned could cost between $100 and $400. If your coils can be accessed in-place, you'll be looking at a lower service cost. If your technician needs to remove the them first, the cost should be around $400. Having the evaporator and condenser coils cleaned can have a significant impact on the efficiency of your system. If your coils are excessively dirty, they won't be able to do their job and your system will have to work harder. Keeping up with the hygiene of these components can save you money in both the short and long-term. For example, replacing evaporator coils can cost anywhere from $650 to $1200.
We are all getting migraines several times a month. I have asthma but not ever as bad as it has been and my 2 year olds dr just informed me she potentially has asthma too. We all get sinus infections regularly and eczema and contact dermatitis. None of us have been this way until recently in our apartment. A roof leak with mold was repaired recently mold was sealed off not removed. We also had lead paint removed from a few window trims this year. I wasn’t here to see if they covered the vents. We had mice too. I vacuum everyday we have hardwood floors no one wears shoes past the font door and I’m getting over a cup full of dirt every time I vacuum. Dust on everything daily. White dust. It’s a 4 room apartment with 1 intake. They are filthy from what I can see when I change the filters. The filters are black after a few months. I feel bad to ask the homeowner to get the system cleaned, can’t afford to move (we live in the city & it’s expensive). I am going to try the shop vac to remove what I can. Any experienced hvac people please give your opinion. Should I just get it done and pay for it myself? We have lived here for 13 years. It’s never been cleaned since ive been here. Is it something I can do with a shop vac? Can i use a wet rag to get the powder dust on the inside of the vents off. One vent has what looks like chunks of dry wall or thick paint sitting in the vent and none of the vents screw into the wall, the screws just fall out. No one ever reinforced the area so the wall just basically crumbles. Kind of useless to spend the money on filters since the air and dust just blows out around the sides of the vents and one of the vents just falls right out of the wall when the heat is turned on. I don’t know why the owner doesn’t fix it. He’s been here to replace filters and saw the condition.
All of you have dentists, you have doctors, you have preachers, you have mechanics. You don’t have to know everything about everything but you have to have people in your life that you can trust. Don’t just open up the phone book and pick a mechanical (HVAC) contractor. Call your friends and family and ask for referrals. There are no black and white (scam or not a scam) answers here.
I am a service technician [since '92].....and as to double filtering.....I have never recommended it. Granted.....it would be noticeably helpful if the fiberglass filters are the main ones used [which I also never recommend.....as long as system can deliver appropriate air flow with a pleated cotton filter...and any decent service tech can check the air flow for proper cfm]. Any particles small enough to pass through a pleated cotton filter are going to pass through a second filter as well....unless the second filters are so tight that the system is starving for air flow. Has anybody ever accidentally put two filters in their automatic drip coffee maker? What if cars used two fuel filters or air filters? I have told some homeowners to try using second filters at each register [the black thin filter material cut-to-fit....same type used in many window air conditioners].....but I only suggest this when I know they will still get at least 400 cfm per ton of air flow [350 absolute minimum]......as some homeowners know others who say it has helped and it gives them a peace of mind knowing they are doing something to help contribute to a solution, so it HAS to help [even though I think it falls in the "one-born-every-minute" category.....similar to duct cleaning].
This is to Blueberry who.wrote.about home rental dust problems on 12/ 06/2016. If you’ve been there 13 years.your landlord has made enough money to have those problems repaired.I would call your city property standards dept. And let them know what.conditions you are having to live.There is no excuse for living in those conditions when most problems like that are easy fixes.Especially if your kids are getting sick. Tell your landlord your.calling City Health Inspector if he doesn’t fix.the problems.
fact is most homes have bad filter racks. when you insert the filter it doesn’t seal well to the sides so some of the air and dust bypass it and end up in the supply ductwork and into the house. Most of the dust in the supply ductwork settles down and doesn’t get blown in the house but some of it does when the blower starts up or when you put a new filter. If you have allergies or other health problems put in an electronic air cleaner, get your ducts cleaned and run the fan as much as you can afford. you can also get an ECM motor installed which is going to be worth it if you want to run the fan 24/7. If you have uninsulated metal ducts take down the ones you can and wash them. Then put them back and seal the joints. Cleaning the ductwork also improves airflow which is important to AC and Heat pump systems for efficiency. An electronic air cleaner will also improve airflow and static pressure because they usually have a much larger filter surface area. An electronic air cleaner also keeps the ac coil clean like new which means better efficiency and no cleaning needed. AC furnaces sometimes grow mold around the coil because of the condensation. Electronic air cleaners should be able to filter mold spores but the best remedy is installing a UV light next to the coil which will kill the mold.

Did not realize cost had gone up so much for this service. Two years ago I had furnace and ducts cleaned at my old house and it was under $400. Now the cost is $700 for this house. I will keep looking for someone to offer a lower price, check them out, and have it done. Or will find the paperwork to see who did it before. I liked this article and did learn some things. Thanks.
If no one in your household suffers from allergies or unexplained symptoms or illnesses and if, after a visual inspection of the inside of the ducts, you see no indication that your air ducts are contaminated with large deposits of dust or mold (no musty odor or visible mold growth), having your air ducts cleaned is probably unnecessary. It is normal for the return registers to get dusty as dust-laden air is pulled through the grate. This does not indicate that your air ducts are contaminated with heavy deposits of dust or debris; the registers can be easily vacuumed or removed and cleaned.
×